yeti 6000 for a Rheem gas furnace
Skor
Member Posts: 2 ✭✭
I used a KillaWatt to make sure it met all the power requirements, and it seems fine, but when I try to use the Yeti my Furnace gets error code 26, which says it thinks Neutral is wired wrong.
Is something wired wrong in the 6000's pure sine wave converter?
Answers
-
Hi @Skor,
Could you send the specs for the furnace? We want to be able to see what exactly the furnace requires to be able to give you the best answer.
-
It's an Econet Enabled Prestige Series Variable Speed Multi Position (R96V)
Model
R96VA0702317MSA
-
Hi @Skor,
Keep in mind, that the Yeti is not grounded the way a normal plug is. If grounded is a requirement for the furnace, which that what it seems like from the user guide, then it more than likely will not work.