If input parameters of HPP input port are respected, does the power source matter?

Options
MFT230
MFT230 Member Posts: 1 ✭✭

I want to charge 1500x from 24v lithium battery bank. 24v is within voltage window. Battery puts out max of 50a so should also be inside Amp window.

Seems too good to be true but would allow me to ditch lead acid tanks, improve portability of the system ... what am I missing?


MFT

Answers

  • jg164
    jg164 Administrator, Moderator Posts: 292 admin
    Options

    @MFT230,

    Always check the user guide or product page for input specs.

    The Yeti 1500X actually has 5 ports that can take an input. Each port has different specs:

    • INPUT
    • 1x High Power Charging port (AC or Solar): 600W Max (14-50V, up to 50A)
    • 2x 8mm charging port (AC or Solar): 150W Max (14-50V, up to 10A); Front face & under lid
    • INPUT/OUTPUT
    • 1x USB-C PD port: 60W Max (5 - 20V, up to 3.0A), regulated

    The 5th port is the module port where the Yeti Link connects to the Yeti X. Here are the Link's input specs:

    PORTS

    • 8mm Charging Port (input): 14 - 22V Do not exceed 150W (10A) per port
    • External Battery Connector (output): 65A Charge Controller
    • External Battery Connector (Input/Output): 10.7-15V. Do not exceed 15V